• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Electric Panel Behind Door

fj80

Sawhorse
Joined
Jan 18, 2016
Messages
230
Location
Virginia
Is an electric panel allowed to be located behind a door (when the door is in the open position)? There would be adequate clear working space in front of the panel when the door is in the closed position.
 
l would say, it depends, nothing prohibits it but Article 110.26 does say that the work space shall be clear at all times.

In reality, it is better than having junk or shelving in front of it.....
 
It also is a hazard if the door can be swung into the electrician when working on the panel
 
I see nothing wrong with the panel being installed behind a door as long as there is access to the panel that meets the working clearances and the panel door is allowed to open 90°. With no plumbing above or below and no potential damage to the panel from the door.

Is the question due to the door hiding the panel?
 
No mention made as to capacity of the panel, how big the room is and whether the door swings away from or over the panel.
 