• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

EMT to FMC

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,041
Location
Somewhere Too Hot & Humid
The range location was changed for this condo kitchen remodel. They used FMC to connect to the EMT for about 18”. What is wrong and why?
555DCCAA-CE5A-41B1-98C6-C3E842B63320.jpeg
 
Back to the OP ... looks like there might be more than 360 degrees of bends in the flex.
 
  • Like
Reactions: ICE
Does the connection need to be accessible? How is it different ... in theory ... from a joint in emt?
 
The issue here is that FMC is only rated at 20 A using it as an equipment grounding conductor, in this case, extending the EMT. This is a grounding issue. This is a 50 amp circuit for a plug-in range. I thought I put this in the electrical section, not sure why I’m getting drywall screw comments.
 