I have a question that seems to be up to interpretation.
I am looking at 2009 IBC Section 1022.1 Exception 1. The wording states “…a stairway is not required to be enclosed when the stairway serves an occupant load of less than 10…
Assume everything else in the Exception is in compliance and only two exit stairs.
So could you have 20 occupants on the second floor and the two exit stairs would only serve 10 and therefore not be required to be enclosed? Or is the reference to a total occupant load of 10 on the second floor?
Definition from 1002 - Occupant Load - The number of persons for which the means of egress of a building or portion thereof is designed.