• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Exception for stair landing for stair higher than 12 feet?

gnarkill283

Registered User
Joined
Nov 15, 2017
Messages
107
Location
New York
We have a 16'4" high stair leading up to a floor which houses back of house stuff like electrical rooms, storage, etc. Is there any exception here for the landing requirement? If there is no exception, can the landing be at 12' and not in the middle of the stair run?
 
If it is purely mechanicals and "true egress" is not required, I would buy it....In other words, could it be a 16' ladder and still meet code?
 
Yes, the landing can occur anywhere in the 12' vertical rise, the stairway does not have to split the change equally.
 
1009.1 General.
Stairways serving occupied portions of a building shall comply with the requirements of this section.


OCCUPIABLE SPACE. A room or enclosed space designed for human occupancy in which individuals congregate for amusement, educational or similar purposes or in which occupants are engaged at labor, and which is equipped with means of egress and light and ventilation facilities meeting the requirements of this code.

Does not sound like it is an occupied space
 