We have an existing 25 unit apartment building (R-2) in town that was damaged by fire. 15 of the units on one end are undamaged and will be put back in service with only fresh paint and carpet. The other 10 units (all on one end) have damage to the floor trusses, so will be demolished to the foundations and rebuilt to match existing.
As I read the 2015 existing building code using the Work Area Compliance Method, I would interpret this project to be a Level 2 alteration since we are replacing structure, windows, systems, etc, but we are modifying less than 50% of the building. (10/25 = 40%) We are re-using the existing foundations.
Is my interpretation correct to this point?
If so, am I correct that 804.2.2 states that adding a fire sprinkler system to the reconstructed portion of the work is not required since the work area is below 50%?
The Building Official and the Fire Marshal have required the new construction be sprinklered. They rejected the work area compliance method argument and stated the 40% of the building that we are rebuilding is considered new construction, therefore must fully follow IBC, not IEBC.
Any insight would be appreciated. I don't mind being wrong, but they haven't convinced me that they are following the requirements of the code.
We plan to provide the sprinkler system in the rebuilt portion of the building regardless, but I need to know if that sprinkler system is above and beyond the minimum requirements.
Thank you for your expertise.
As I read the 2015 existing building code using the Work Area Compliance Method, I would interpret this project to be a Level 2 alteration since we are replacing structure, windows, systems, etc, but we are modifying less than 50% of the building. (10/25 = 40%) We are re-using the existing foundations.
Is my interpretation correct to this point?
If so, am I correct that 804.2.2 states that adding a fire sprinkler system to the reconstructed portion of the work is not required since the work area is below 50%?
The Building Official and the Fire Marshal have required the new construction be sprinklered. They rejected the work area compliance method argument and stated the 40% of the building that we are rebuilding is considered new construction, therefore must fully follow IBC, not IEBC.
Any insight would be appreciated. I don't mind being wrong, but they haven't convinced me that they are following the requirements of the code.
We plan to provide the sprinkler system in the rebuilt portion of the building regardless, but I need to know if that sprinkler system is above and beyond the minimum requirements.
Thank you for your expertise.