JCraver
Sawhorse
Given:
2015 IBC, IEBC, IFC
Existing 2-story Type V, non-sprinkled, built 1920's
~3,000 sf per story
1st floor - B (Chiropractor's Office)
2nd floor - vacant R-3, proposed Level 3 Alteration (single-family, building owner and his wife want to move in. NOT live-work, they rent to the chiropractor)
2nd floor has it's own enclosed stair from the street to the dwelling unit. No openings anywhere between floors.
IEBC:
904.1 Automatic sprinkler systems. An automatic sprinkler system shall be provided in a work area where required by Section 804.2 or this section.
804.2 Automatic sprinkler systems. Automatic sprinkler systems shall be provided in accordance with the requirements of Sections 804.2.1 through 804.2.5. Installation requirements shall be in accordance with the International Building Code.
804.2.2 Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2. In buildings with occupancies in Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2, work areas that have exits or corridors shared by more than one tenant or that have exits or corridors serving an occupant load greater than 30 shall be provided with automatic sprinkler protection where all of the following conditions occur:
1. The work area is required to be provided with automatic sprinkler protection in accordance with the International Building Code as applicable to new construction; and
2. The work area exceeds 50 percent of the floor area.
Exception: If the building does not have sufficient municipal water supply for design of a fire sprinkler system available to the floor without installation of a new fire pump, work areas shall be protected by an automatic smoke detection system throughout all occupiable spaces other than sleeping units or individual dwelling units that activates the occupant notification system in accordance with Sections 907.4, 907.5 and 907.6 of the International Building Code.
So no sprinklers required, correct? I can't find anything anywhere that says a remodeled R-3 must be sprinkled..
2015 IBC, IEBC, IFC
~3,000 sf per story
IEBC: