G2arch
Member
Have a client bought a building currently configured as such.
Occupancy B
Fully Sprinklered
Two Stories at 3500 sf each
Unenclosed stair inside building about 1/3 distance from front of building
Enclosed stair at back of building.
He would like to configure it as such.
First floor stays B. First floor would still have two exits, out front door and out back enclosed stair.
Second floor front 1500sf is B occupancy access only from the open stair.
Second floor back 2000sf is to be an R-2 Dwelling unit access only from enclosed stair.
Jurisdiction current code is IBC 2012.
I can meet the requirements of Table 1021.2(1) for the R-2 dwelling as I am less than 4 dwellings and less than 125 max exit access travel distance.
I can meet the occupant load but not the exit access travel distance Per Table 1021.2(2) for the second floor B occupancy. Maximum Exit access travel distance 75 feet. I can not make it down the stairs and to an first floor exit in this distance. Therefore, am I correct that this configuration will not meet IBC 2012 code?
Second Question, The jurisdiction is considering adopting IBC 2018. IBC 2018 Table 1006.3.3(2) for Stories with One Exit has been changed to read 75ft common path. I can get to the bottom of the open stair in less then 75feet where one would have two ways to go, either the front exit or the back exit. So it does meet IBC 2018 code?
Thanks
Ken
Occupancy B
Fully Sprinklered
Two Stories at 3500 sf each
Unenclosed stair inside building about 1/3 distance from front of building
Enclosed stair at back of building.
He would like to configure it as such.
First floor stays B. First floor would still have two exits, out front door and out back enclosed stair.
Second floor front 1500sf is B occupancy access only from the open stair.
Second floor back 2000sf is to be an R-2 Dwelling unit access only from enclosed stair.
Jurisdiction current code is IBC 2012.
I can meet the requirements of Table 1021.2(1) for the R-2 dwelling as I am less than 4 dwellings and less than 125 max exit access travel distance.
I can meet the occupant load but not the exit access travel distance Per Table 1021.2(2) for the second floor B occupancy. Maximum Exit access travel distance 75 feet. I can not make it down the stairs and to an first floor exit in this distance. Therefore, am I correct that this configuration will not meet IBC 2012 code?
Second Question, The jurisdiction is considering adopting IBC 2018. IBC 2018 Table 1006.3.3(2) for Stories with One Exit has been changed to read 75ft common path. I can get to the bottom of the open stair in less then 75feet where one would have two ways to go, either the front exit or the back exit. So it does meet IBC 2018 code?
Thanks
Ken