Can an areaway be used as an exterior exist stair?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I suppose it depends on the size of the areaway. How large is it, and would the space be large enough to provide open airflow to prevent the accumulation of smoke. The challenge as I see it is in Sec. 1027.3.
2020 NYBC1027.3 Open Side
Exterior exit stairways and ramps serving as an element of a required means of egress shall be open on not less than one side, except for required structural columns, beams, handrails and guards. An open side shall have not less than 35 square feet (3.3 m2) of aggregate open area adjacent to each floor level and the level of each intermediate landing. The required open area shall be located not less than 42 inches (1067 mm) above the adjacent floor or landing level.
Stair and areaway pictured belowI suppose it depends on the size of the areaway. How large is it, and would the space be large enough to provide open airflow to prevent the accumulation of smoke. The challenge as I see it is in Sec. 1027.3.
2020 NYBC1027.3 Open Side
Exterior exit stairways and ramps serving as an element of a required means of egress shall be open on not less than one side, except for required structural columns, beams, handrails and guards. An open side shall have not less than 35 square feet (3.3 m2) of aggregate open area adjacent to each floor level and the level of each intermediate landing. The required open area shall be located not less than 42 inches (1067 mm) above the adjacent floor or landing level.
No elevations just yet but, there will be some window openings above the well. It is a small A3 (O.L. = 18 people) occupancy.Any overhangs or openings directly above the stairwell? An elevation is likely to provide more detail.
Also, what occupancy is this?
Keep in mind Sec. 303.1.1; you will actually likely be a Group B occupancy given such a low OL.It is a small A3 (O.L. = 18 people) occupancy.