In addition to Table 602 review Section 705.8 for allowable openings. Where openings are not permitted the glazing if provided shall be Fire-resistance rated (see definition below).
Fire Separation Distance is measured to the center of the public way (street or sidewalk).
TABLE 602
FIRE-RESISTANCE RATING REQUIREMENTS FOR EXTERIOR WALLS BASED ON FIRE SEPARATION DISTANCE
FIRE SEPARATION DISTANCE. The distance measured from the building face to one of the following:
1. The closest interior lot line.
2. To the centerline of a street, an alley or public way.
3. To an imaginary line between two buildings on the lot.
The distance shall be measured at right angles from the face of the wall.
Fire-rated glazing can be of two types—fire-resistance rating or fire protection rating.
1) Fire-resistance rated glazing is tested to ASTM E119 or UL 263, may be used in walls and is not considered as an opening.
2) Fire-protection-rated glazing is tested to NFPA 257 or UL 9, and is usually in doors or limited size window openings in fire barriers and fire partitions