This question could relate to many buildings, but let’s assume:
Some of what I have found in 2015 IBC:
- 5-story apartment building
- 60 feet in height
- Type III wood construction
- Loadbearing 2-hour exterior walls with FRT plywood sheathing
- No tight fire separation distances
- 3-coat 7/8-inch cement plaster exterior wall finish
Some of what I have found in 2015 IBC:
- 2601.1 says See Chapter 14 for requirements for exterior wall finish and trim.
- 1406.2 says Combustible exterior wall coverings shall comply with this section. Exception: Plastics complying with Chapter 26.
- 2603.5.2 requires a thermal barrier between foam plastic and the building interior, which in this case is the cement plaster.