Forum Coordinator
Below is the code section from IRC 2009.
If a municipality deems the frost depth to be 36". Does that mean that the foundation wall must extend below 36" or just the bottom of the footer?
It is our interpretation that the foundation wall must extend below the frost depth of 36" which means the top of the footer can never be any shallower than 36" to the top of it. The thicker the footer, the deeper you must go.
How do you interpret this?
R403.1.4.1 Frost protection. Except where otherwise
protected from frost, foundation walls, piers and other
permanent supports of buildings and structures shall be
protected from frost by one or more of the following methods:
1. Extended below the frost line specified in Table
R301.2.(1);
2. Constructing in accordance with Section R403.3;
3. Constructing in accordance with ASCE 32; or
4. Erected on solid rock.
1. Protection of freestanding accessory structures
with an area of 600 square feet (56m2) or less, of
light-frame construction, with an eave height of
10 feet (3048mm)or less shall not be required.
2. Protection of freestanding accessory structures
with an area of 400 square feet (37 m2) or less,
of other than light-frame construction, with an
eave height of 10 feet (3048 mm) or less shall
not be required.
3. Decks not supported by a dwelling need not be
provided with footings that extend below the
frost line.
Footings shall not bear on frozen soil unless the frozen
condition is permanent.
R301.2.(1);
not be required.
frost line.