• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Furniture in door maneuvering clearance

Tim Mailloux

Registered User
Joined
Feb 12, 2018
Messages
769
Location
Hartford CT
2016 CT State Building code (based on 2012 IBC)

ANSI A117.1 2009 section 404.2.3 Maneuvering Clearances required a 60” x 54” clear floor space for the forward approach at a 36” door (figure a Front approach, Pull side). I have a small conference room where the corner of the conference room table falls within this clear floor space, and another small conference room where one of the conference table chairs just falls into this clear floor space. Is movable furniture exempt from this requirement?
 
Have them push it over a few inches, if it gets pushed back after you leave, it is their own liability.
 
furniture is typically not "fixed" in place.
Shelving displays less than 5'9" are seldom "fixed in place", however they would not be exempt from clear isle width, clear floor space, etc. due to not being "fixed"

Table needs moved, but don't make a big deal of it either.
 
Accessibility is part of the building code, just like exiting is part of the building code.
  • If a room occupant takes a sofa and pushes it up against an exit door, that would be a violation of the exiting portion of the building code. In this example, neither the architect nor the contractor is responsible for the violation.
  • Same with anyone who places furniture in a way that violates accessibility portion of the building code.
 
I believe that no matter what kind of furniture is moving or not, you still have to free up space, because in the case when you need to quickly evacuate, this can decide the fate of the people who work for you. This is definitely a violation. Perhaps you should buy a smaller table or more compact chairs.
 
I believe that no matter what kind of furniture is moving or not, you still have to free up space, because in the case when you need to quickly evacuate, this can decide the fate of the people who work for you. This is definitely a violation. Perhaps you should buy a smaller table or more compact chairs.
Yes, I must really agree that this is a serious violation. In my opinion, you should not risk the lives of your people and just replace furniture or change the arrangement. Although it will most likely be easier to simply replace the furniture. However, I don't know where you can buy such furniture. Perhaps you can find everything you need on the service https://thekairoscollective.com/furniture/tables.html , although in my opinion the prices there are a little too big, but the product is unique and quite beautiful. I think you can definitely find the furniture you need there if you really think about replacing it. Although I may be mistaken and such furniture is not a violation if it can be simply moved quickly.
 
Accessibility is part of the building code, just like exiting is part of the building code.
  • If a room occupant takes a sofa and pushes it up against an exit door, that would be a violation of the exiting portion of the building code. In this example, neither the architect nor the contractor is responsible for the violation.
  • Same with anyone who places furniture in a way that violates accessibility portion of the building code.

Not responsible but doesn't prevent still being named/drawn into the claim.
 
Not responsible but doesn't prevent still being named/drawn into the claim.

ADAGuy, nothing prevents anyone from being drawn into any claim. What are you suggesting that architects and contractors do as a best practice in a situation where furniture is put in place after they are off the project?

On the other hand, if the project is still in design phase and the architect is representing to the owner that they can put furniture where they shouldn't in order to achieve program goals, that is bad-faith design.
 
ADAGuy, nothing prevents anyone from being drawn into any claim. What are you suggesting that architects and contractors do as a best practice in a situation where furniture is put in place after they are off the project?

On the other hand, if the project is still in design phase and the architect is representing to the owner that they can put furniture where they shouldn't in order to achieve program goals, that is bad-faith design.

Include a signed disclaimer by the client indicating his "acceptance of liability and indemnification for" his use (whether compliant or non) of the space at the completion of the project. You are responsible for the built space, not the use (other then for its intended purpose[debateable]) of the space created.
 
I have had plans submitted showing furniture in the spaces that would be a violation (accessibility and MOE). I don't stamp them. I have never had anyone argue, they just remove the furniture.
 
Include a signed disclaimer by the client indicating his "acceptance of liability and indemnification for" his use (whether compliant or non) of the space at the completion of the project. You are responsible for the built space, not the use (other then for its intended purpose[debateable]) of the space created.
Good suggestions, but most of my clients would never sign such a document. About the best I can do is include a statement in my original contract that we design only to the [specified local code] and the physical design requirements published in the 2010 ADAS, as it applies to the fixed elements of the building showed in the approved plans, and specifically excluding any post C-of-O furnishings or operations.
 
Consider Ikea as a source. indicate N.I.C and show dotted any furniture not in your contract.
 
I always make the statement on my final inspection report "no furniture was present at the time of the inspection" in dining and assembly areas and sometimes take a picture. I never thought of doing it for everywhere else. Maybe I should.
 