1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Gas boiler heating problem

Discussion in 'Plumbing Codes' started by William Clements, Oct 17, 2018.

  1. William Clements

    William Clements Registered User

    Joined:
    Oct 17, 2018
    Messages:
    4
    Likes Received:
    1
    Heating is done by a gas boiler,(old but works well) and water is heated via an indirect coil in the cylinder with a thermostat on the exterior about 2/3 way up from the bottom. I can never seem to get the temperature of the hardware right, it is either far too hot or just warm enough, it is noticeable when the shower is in use, I have to turn the shower control way down or full up.
    My first thought was the cylinder stat, so I replaced it, but no difference.
    The issue happens in the summer as well when the central heating is off, and the boiler is only in use for hot water supply.
    Obviously, when it is too hot I am wasting gas, not good. Need suggestions on this or else should I call plumbing repair service?
     
  2. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    976
    Likes Received:
    123
    I'm afraid it's the nature of the beast. A separate domestic water heater is your best bet.
     
    William Clements likes this.
  3. William Clements

    William Clements Registered User

    Joined:
    Oct 17, 2018
    Messages:
    4
    Likes Received:
    1
    Thanks
     
  4. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    112
    Likes Received:
    34
    Run the thermostat higher than you need and put in a ASSE 1017 tempering valve to control (limit) the temperature to the hot water distribution system. This is the way it has been done ever since Holby valves came to be in 1930. I am not saying that Holby is the brand of valve you need to use but they were probably the first ones to design such valves (in the US). Many other brands are available.
     
  5. jwilly3879

    jwilly3879 Sawhorse

    Joined:
    Apr 2, 2010
    Messages:
    151
    Likes Received:
    37
    This is also called a tempering valve.
     
    rogerpa likes this.
  6. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    112
    Likes Received:
    34
    that's what i said: "a ASSE 1017 tempering valve" per IPC Section 613.1 (2012 edition)
     