• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

GFCI Protection for 208/3ph Receptacles in Commercial Kitchens

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,041
Location
Somewhere Too Hot & Humid
One of the things that really stands out in the 2017 NEC is the requirement for receptacles 50A and less for single-phase and 100A or less for 3-phase in commercial kitchens to be GFCI protected. It reads like this:


(B) Other Than Dwelling Units. All single-phase receptacles
rated 150 volts to ground or less, 50 amperes or less and three-phase
receptacles rated 150 volts to ground or less,
100 amperes or less installed in the following locations shall
have ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Kitchens
(3) Rooftops
Exception: Receptacles on rooftops shall not be required to be readily
accessible other than from the rooftop.
 