• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Help with Sprinklers in- high-rise residential buildings IBC

Irakli

Registered User
Joined
Nov 21, 2018
Messages
3
Location
Republic Of Georgia
Shortly
in my Country we just approved low witch is close similar to IBC 2018. In my company we are preparing to built high-rise apartment building with accordance to mentioned low

Question
As per IBC sprinklers should be installed ALL OVER building ? what about dwelling units ? lets say bad rooms, living room....? how you people deal with it ? If you imagine you have 500 dwelling units equipped with sprinklers, all experienced in this field knows that soon or later at least one of sprinklers will activate (due to technical issues and not fire , lats say one owner decides to change light bulb, he hires electrician and this electrician or any other worker accidentally brakes the glass of sprinkler with hand tool or something like that, or due to poorly made connection ...) and then all water spreads all over apartment . Just imagine the owner payed thousands and thousands for TV..... , even apartment below will be partially flooded , lots of problems ?

I'm ok with sprinklers all over building (except electrical rooms ......) in corridors and so on but inside apartments ???

Please advice how you deal or how you imagine to deal with sprinklers inside apartments ?? is there any way to substitute sprinklers with detection or announcement or with anything else

your opinion is highly appreciated
thanks
 
How many stories.???

What type of constitution material ?


Yes install in the apartment units.

Yes a few rooms in the apartment might have an exception.

We install per NFPA 13
 
How many stories.???

What type of constitution material ?


Yes install in the apartment units.

Yes a few rooms in the apartment might have an exception.

We install per NFPA 13
Hi

31 stories (1001 meter)
exterior walls -concrete, internal walls concrete plus gypsum
 
Yes sprinklers required in the units, follow NFPA 13 for design,

Plus IBC chapter 4 for high rise
 
Use concealed heads to avoid accidental breakage