1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

High rise fire and life safety systems

Discussion in 'Electrician Talk' started by johnniekayak, Jul 11, 2019.

  1. johnniekayak

    johnniekayak Registered User

    Joined:
    Jul 11, 2019
    Messages:
    2
    Likes Received:
    0
    Hello I'm new to this forum but hoping I can get some answers.
    I've been scouring the national building code of Canada looking for fire ratings. I need to know when I have to use 2 hour fire rated cable in a 23 storey building with a 2 hour rated riser shaft.
    Fire alarm cables, emergency distribution cables or cables from the generator to the ATS for the fire pump?
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,036
    Likes Received:
    996
    Welcome

    I think there is one person that speaks north of the border on the forum,

    Plus sense the code book is not online
     
  3. Ty J.

    Ty J. Registered User

    Joined:
    Aug 2, 2017
    Messages:
    465
    Likes Received:
    189
  4. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,614
    Likes Received:
    422
    If it is in a rated riser, you do not need to rate the cable itself.

    I think Manitoba is still on the 2010 NBCC...

    I'm guessing the building must be of non-combustible construction. In that case look at 3.1.5.18. for requirements of wires and cables.

    Typically, you just need to firestop the cable where it breaches the rated separation.

    Specific requirements for the fire alarm system will be in CAN/ULC-S524. Fire pumps is NFPA 20.
     
  5. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,327
    Likes Received:
    299
    Thanks TM, you the "man".
     
  6. johnniekayak

    johnniekayak Registered User

    Joined:
    Jul 11, 2019
    Messages:
    2
    Likes Received:
    0
    thx for the info I found the rules I needed.
    Underground to the 2hr rated shafts or 2hr fire rated room where the fire pump and ATS are located can be run in pvc(DBII) no fire rating required. Is this assumption correct?
     
  7. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,614
    Likes Received:
    422
    For a non-metallic raceway, look at 3.1.5.20. to make sure your product meets the required testing criteria.
     