I have a one way horizontal exit, the horizontal exit double doors have a capacity of 455 people but I only have 225 people exiting thru them, in one direction only. But according to 1026.4 the size of the refuge area is to be based on the capacity of the doors, not the egress load thru those doors. This is going to result in an area of refuge twice as large as it needs to be. I could reduce the size of the doors to a capacity more inline with the egress load, but architecturally we want these double doors to match all the other pairs of double doors in the area.
on second thought.....These doors will be on hold opens, what if one leaf had no hardware so it couldn't be used for exiting, then only the leaf with hardware would get counted into the capacity calculation and area of refuge sizing.