1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

How to vent a floor sink when the nearest wall is ~10' away?

Discussion in 'Commercial Plumbing Codes' started by Michael.L, Jun 7, 2018.

  1. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    128
    Likes Received:
    19
    I'm laying out the floor plan for a small cafe. There will be a coffee bar at the service counter with a 3-compartment sink. The 3-comp sink's drain will be indirectly plumbed to a floor sink below with a required air gap. But the closest wall is 9.6 feet from the location of this floor sink. Is it acceptable for the vent to be that far from the floor sink trap? Do I just upsize the fixture arm drain pipe to ensure that the vent connection opening remains above the trap weir?
     
  2. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    724
    Likes Received:
    65
    Why not use an Auto Air Vent?
     
  3. Sifu

    Sifu Gold Member

    Joined:
    Sep 3, 2011
    Messages:
    935
    Likes Received:
    49
    Combination waste and vent.
     
  4. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,643
    Likes Received:
    488
    If the 3 compartment sink is also being used as a food prep sink then it should be going to a grease interceptor

    3 " drain will allow 12 feet from the trap to the vent
     
    Michael.L and Pcinspector1 like this.
  5. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    128
    Likes Received:
    19
    It's not a food prep sink, but it will be used to wash out milk steaming jugs and blender jars. It will be drained to our grease interceptor.

    Are you sure? According to this graphic, a 3" drain will only allow a max trap arm length of 6 feet, and that I'd need a 4" or larger to get the max trap arm length to 10 feet.

    [​IMG]
     
    #5 Michael.L, Jun 7, 2018
    Last edited: Jun 7, 2018
  6. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    128
    Likes Received:
    19
    One reason is that they tend to make a noise like a "whoopie cushion." Not exactly what you want customers to hear at your cafe's service bar.
     
  7. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    128
    Likes Received:
    19
    Like this?
    [​IMG]

    I don't know if the existing sewer line under the slab is deep enough to allow this type of configuration.
     
  8. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    724
    Likes Received:
    65
    I can understand that.

    mtlogcabin is spot on, if your using local jurisdiction uses IPC then you will be okay. Chapter 9, Venting from the IPC allows up to 12ft when using 3" drain at 1/8" slope.
     
    Michael.L likes this.
  9. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,270
    Likes Received:
    194
    2012 IPC TABLE 909.1
     
    Michael.L likes this.
  10. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    128
    Likes Received:
    19
    Thank you for the code reference. That's always better than random images culled from the interwebs. :p

    My apologies to Mtlogcabin for doubting you!
     
  11. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    2,153
    Likes Received:
    170
    What you show is an island vent, commonly used on residential kitchens.
     
  12. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    128
    Likes Received:
    19
    Our service bar will essentially be an island. I'm curious: why plumbers would install an island vent like that rather than just upsizing the trap arm pipe to 3" (or 4")?
     
  13. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,643
    Likes Received:
    488
    My apologies for not including the code reference table
     
  14. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    64
    Likes Received:
    16
    AAV = Air Admittance Valve
     