IBC Separated Occupancy A-3 & A-5
LSTOPS39
United States
I am working on an existing pole barn (post-frame) structure remodel where a portion of the space is classified as A-3 assembly for the lounge/ light kitchen area, and A-5 assembly for the remaining covered pavilion open air area. I am being asked to provide fire separation information between the two areas. Does anyone know what is required? 1 hour, (2) layers of 5/8" type x? I typically work in residential, so this is new territory! Thank you.
Need a whole lot more information...
Code adopted, construction type, sprinklers, building area, fire areas, etc.
Very difficult to discern why the fire rated wall is needed, thus impossible to determine the requisite fire rating or type of fire-rated wall assembly that is required.
Need more info needed, but my guess is 1029.1.1.1 may be applicable.
2018 IBC
[F] 903.2.1.5 Group A-5.
An automatic sprinkler system shall be provided for all enclosed Group A-5 accessory use areas in excess of 1,000 square feet (93 m2).
[F] 903.2.1.5.1 Spaces under grandstands or bleachers.
Enclosed spaces under grandstands or bleachers shall be equipped with an automatic sprinkler system in accordance with Section 903.3.1.1 where either of the following exist:
1. The enclosed area is 1,000 square feet (93 m2) or less and is not constructed in accordance with Section 1029.1.1.1.
2. The enclosed area exceeds 1,000 square feet (93 m2).
1029.1.1.1 Spaces under grandstands and bleachers.
Spaces under grandstands or bleachers shall be separated by fire barriers complying with Section 707 and horizontal assemblies complying with Section 711 with not less than 1-hour fire-resistance-rated construction.
1. Ticket booths less than 100 square feet (9.29 m2) in area.
2. Toilet rooms.
3. Other accessory use areas 1,000 square feet (92.9 m2) or less in area and equipped with an automatic sprinkler system in accordance with Section 903.3.1.1.