• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

K Class

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
So a fully self contained fryer/ ventless meeting 96 and IMC

Does it require a K Class fire extinguisher
 
906.4 Cooking Equipment
Fire extinguishers provided for the protection of cooking equipment shall be of an approved type compatible with the automatic fire-extinguishing system agent. Cooking equipment involving solid fuels or vegetable or animal oils and fats shall be protected by a Class K-rated portable extinguisher in accordance with Sections 906.1, Item 2, 906.4.1 and 906.4.2 as applicable.
 
Yep, plan B in the event of failure of the required extinguishing system. Pretty sure there is a requirement in 96 for the supplemental portable K also or it’s in NFPA 17A for the extinguishing agent for commercial cooking equipment. Don’t have access on the codes right now......
 
Ok, no hood but the unit has a built-in wet chemical agent, fill cylinder using only Amerex KP Wet Chemical Agent (6GT015)
 