• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

LPG Tank and Gas Line

Alias

Registered User
Joined
Oct 26, 2009
Messages
1,649
Location
State of Disbelief
~ = ~ = ~

Ms. Sue,

I cannot see your posted pics. here at work, because of filters.

The IRC, Ch. 24 - Piping system installation, ...has language in

it that models the IFGC & the IFC......Refer to Ch. 61 in the IFC,

that says "refer to the IFGC for compliance & installation requirements."

The IFGC does not prohibit installation above ground, but DOES have

requirements for protection of such piping systems.

As I understand the requirements and referenced standards, they can

install an LPG piping system "above ground", but must install it with

safeguards to prevent damage to \ protection of that system.

Hope this helps ! :cool:

~ = ~ = ~
 
How about this from the 2012 IRC (references the Furel Gas Code also);

G2415.9

(404.9) Above-ground piping outdoors.



All piping installed outdoors shall be elevated not less than 31/2

inches (152 mm) above ground and where installed across roof surfaces,

shall be elevated not less than 31/2 inches (152 mm)

above the roof surface. Piping installed above ground, outdoors, and

installed across the surface of roofs shall be securely supported and located

where it will be protected from physical damage. Where passing through an

outside wall, the piping shall also be protected against corrosion by

coating or wrapping with an inert material. Where piping is encased in a

protective pipe sleeve, the annular space between the piping and

the sleeve shall be sealed.
 
2009 Michigan Residential Code Section G2415.7 (same as 2012 IRC). Michigan is not scheduled to (tentatively) adopt the 2012 version until May 2016.
 
Alias, Check the local pub, I heard the Ditch-witch was having battery problems!

IFGC 404.9 Minimum burial depth is 12" below grade. May be the property owners responsibility to have the line buried. No worries if tank is not supplied except for the gas line trip hazard.

If its the GASco, they may not have the equipment to bury the gas line or may be relying on a sub-contractor to do the work.

pc1
 
Well, here is the update. The line is still laying on the grass and no one has been back to bury the line. It is not protected in any way. The grass is getting long and the snowbird likes to get on her riding mower to keep her grass mowed. :mrgreen:

Sue
 
Pcinspector1 said:
If its the GASco, they may not have the equipment to bury the gas line or may be relying on a sub-contractor to do the work.
Really, no pick and shovel?