• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Maximum Area of Exterior Wall Openings/ IBC Table 705.8

jrandol6

Registered User
Joined
Jan 27, 2020
Messages
1
Location
The Marble City
I am working on an apartment building in Tennessee which is located 7 feet from the property line at it's closest point. The exterior walls are 1 hour fire rated (per Table 602) and is sprinklered (NFPA 13R), however, the plans reviewer believes that per table 705.8 (Maximum Area of Exterior Wall Openings...) that a type 13R sprinkler system is classified as Unprotected, Nonsprinklered which only allows 10% of opening area. He is arguing if you see the footnotes, only a NFPA 13 sprinkler system would qualify as sprinklered. It seems counter intuitive that a type 13R sprinkler system is as good as not sprinklered.

If the openings are reduced to fit within the 10% allowable, windows will be too small to meet egress requirements. Any ideas for maintaining openings other than switching to a NFPA 13 sprinkler system? Rated glazing?
 