• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Metal alternative for 2x4 truss rat runs when penetrating 1 hour fire wall

RPM001

Registered User
Joined
Apr 17, 2019
Messages
14
Location
Ft. Lauderdale FL
I have 2x4 permanent truss bracing at the bottom chord (rat runs) that penetrate 1hour drywall tenant separation walls (and the inspector won't pass it with wood penetrating). Has anyone ever used any type of steel/ metal beams instead of 2x4s in certain areas? Or has anyone every built a metal sleeve to encapsulate the rat runs where they penetrate 1 hour separation walls?
 
You should not need the bottom chord bracing (rat runs) with sheet rock installed on the ceiling. Check with the truss engineer. You should be able to remove it where the tenant separation walls are.
 

Attachments

  • 1603830823876.png
    1603830823876.png
    32.3 KB · Views: 7
Some of the web members look long enough to need lateral bracing. It could be broken at the tenant separation walls as long as there diagonal bracing is provided in each unit to prevent racking.

It might be worthwhile to see if the inspector would accept fire-retardant treated wood for the penetrating bracing.
 