aaron@rollingsarchitects.
REGISTERED
IBC 2015, We are designing a restaurant to go in a mixed use single story strip mall. Size will required sprinkling of the space. We want to create a fire area utilizing 2 hour rated fire barriers and only sprinkle our space. The space will have exits out the front and back. The local fire department is stating the owner will have to install sprinklers in the entire building not just our fire area.
IBC 2015 903.2.1 states "throughout the story where the fire areas containing group A2 is located" 903.2.1.2 states "sprinkler shall be provided for fire areas containing Group A-2"
Do we need to sprinkle the whole building (cancels project) or just the space?
I appreciate your help.
Thank you,
AAron
IBC 2015 903.2.1 states "throughout the story where the fire areas containing group A2 is located" 903.2.1.2 states "sprinkler shall be provided for fire areas containing Group A-2"
Do we need to sprinkle the whole building (cancels project) or just the space?
I appreciate your help.
Thank you,
AAron