1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

MSS SP-58 (compliant pipe support?)

Discussion in 'Commercial Fuel Gas Codes' started by Darren Emery, May 9, 2013.

  1. Darren Emery

    Darren Emery Sawhorse

    Joined:
    Oct 20, 2009
    Messages:
    438
    Likes Received:
    2
    IFGC references MSS SP-58 for piping support. Unfortunately, that is one of the many referenced standards I do not have. Would you consider this compliant gas line support?

    View attachment 1786

    View attachment 1786

    /monthly_2013_05/572953e887980_Gaslinetreatedblocks.jpg.3fb6359c205f7d00114fdfce1b3c0cda.jpg
     
  2. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    798
    Likes Received:
    48
    not at all an authority on this but I believe the blocks need to be secured to the roof.
     
  3. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,739
    Likes Received:
    539
    Will not work in my area. Are you in a seismic area?301.12 Seismic resistance.

    When earthquake loads are applicable in accordance with the International Building Code, the supports shall be designed and installed for the seismic forces in accordance with that code.
     
  4. Darren Emery

    Darren Emery Sawhorse

    Joined:
    Oct 20, 2009
    Messages:
    438
    Likes Received:
    2
    Seismic Category B here in Kansas
     
  5. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,539
    Likes Received:
    200
    : - :

    From the `06 IBC, Section 407.2 - Design and installation:

    "Piping shall be supported with pipe hooks, metal pipe straps,

    bands, brackets, or hangers suitable for the size of piping, of

    adequate strength and quality, and located at intervals so as

    to prevent or damp out excessive vibration........Piping shall be

    anchored to prevent undue strains on connected equipment

    and shall not be supported by other piping.......Pipe hangers

    and supports shall conform to the requirements of MSS

    SP-58 and shall be spaced in accordance with :Next('./icod_ifgc_2006f2_4_par176.htm')'>Section 415.

    Supports, hangers, and anchors shall be installed so as not

    to interfere with the free expansion and contraction of the

    piping between anchors........All parts of the supporting equipment

    shall be designed and installed so they will not be disengaged

    by movement of the supported piping."

    There's more to this project than just the piping supports.

    Someone will need to address the fasteners that would be

    attached to the roof.



    : - :
     