NEC 2017

cda

SAWHORSE
Joined
Oct 19, 2009
Messages
20,962
Location
Basement
Does NEC 2017 talk about relocatable taps/ strip outlets??

If so where?? Not finding it, but than I try to stay out of NEC


Thank you
 
Power strips are not regulated by the NEC, other than they may not be used in place of fixed wiring (NEC 400.8).

Permitted uses will be regulated by the listing under which they are produced and labeled (i.e. UL listing).
 
From IFC


605.4 Multiplug adapters. Multiplug adapters, such as cube adapters, unfused plug strips or any other device not complying with NFPA 70 shall be prohibited.
605.4.1 Power tap design. Relocatable power taps shall be of the polarized or grounded type, equipped with overcurrent protection, and shall be listed in accordance with UL 1363.
 