• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

New Fire Water Supply Line

north star

Sawhorse
Joined
Oct 19, 2009
Messages
4,596
+ + * + +

Greetings all !

I am reviewing plans for a military facility......The plans indicate
a new Fire Water Supply Line ( 6" ) that will enter the property
and then in to one of the facility bldgs.......I do not see any type
of "Shut Off Valves" from where the municipal water supply line
is "tapped" at the street, nor anywhere along the entire length
of the piping run........There is also a FDC line that will begin
close to the facility property line & be installed parallel along
side of the new 6" Fire Water Supply Line.......There are no
"Shut Off Valves" indicated on this piping either !


QUESTION: Is it "required by Code" to have a "Shut Off Valve"
installed downstream immediately after the municipal line is
"tapped", and also, ...before it enters the facility bldg. ? :confused:
If so, ...can you please provide the Code section or section ?

We are currently using the `15 I-Codes, and the Unified Facilities
Criteria ( UFC ) Codes.

Thank you for your assistance !

+ + * + +

 
Required as referenced above.

From a practical standpoint, if not provided, how would you stop flow during a line break, faulty/damaged sprinkler head, sprinkler discharge after fire is out, etc.
 
+ + = + +

Much Thanks **Builder Bob** !

**Ty J.**, ...with the piping design as it is currently

indicated on the plans, the only recourse to the facility
personnel would be to call the municipal water
supplier and request a "turn off"........That most probably
would not be quickly, hence, that is why I have
requested assistance from the good people on this
Forum.

I will include the Code requirements listed above in my
Comments back to the RDP's.

Thanks again ya'll ! :D

+ + = + +
 
Our public works installs a shut off at the curb stop for all water lines including fire. All valves shall be monitored
[F] 903.4.1 Monitoring.
Alarm, supervisory and trouble signals shall be distinctly different and shall be automatically transmitted to an approved supervising station or, when approved by the fire code official, shall sound an audible signal at a constantly attended location.

Exceptions:

1. Underground key or hub valves in roadway boxes provided by the municipality or public utility are not required to be monitored.

2. Backflow prevention device test valves located in limited area sprinkler system supply piping shall be locked in the open position. In occupancies required to be equipped with a fire alarm system, the backflow preventer valves shall be electrically supervised by a tamper switch installed in accordance with NFPA 72 and separately annunciated.
 
No back flow preventer required where it comes on property or elsewhere in the system????
 
Plus just to tap the city main

Seems like you need a valve in order to make the connection
 