• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

NFPA 80 section 5.2.4.2

In the hospitals and nursing homes it is supposed to be enforced.





2016:

5.2.4.2


As a minimum, the provisions of 5.2.3 shall be included in the periodic inspection and testing procedure.


2013


5.2.4.2


As a minimum, the provisions of 5.2.3 shall be included in the periodic inspection and testing procedure.


2010



5.2.3 Functional Testing.


5.2.3.1
Functional testing of fire door and window assemblies


shall be performed by individuals with knowledge and understanding

of the operating components of the type of door

being subject to testing.



2007


5.2.3 Functional Testing.

5.2.3.1
Functional testing of fire door and window assemblies

shall be performed by individuals with knowledge and understanding

of the operating components of the type of door

being subject to testing.
 
Is this code adopted in California?
1) It is a standard and not a code, and 2) yes, the 2016 edition is listed as a reference standard in Chapter 35 of the CBC, and it indicates the locations where it is referenced in the CBC.
 