1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

No pull stations in Virginia

Discussion in 'Commercial Fire Codes' started by S.Johnson326, Sep 6, 2019.

  1. S.Johnson326

    S.Johnson326 Registered User

    Joined:
    Sep 5, 2019
    Messages:
    2
    Likes Received:
    0
    I recently was in a high rise office building in Virginia and noticed there weren't any manual pull stations anywhere in the building. I looked at the annunciator and pull stations wasn't listed as one of the devices. I went online and looked in the IBC 2015 edition and it states that manual stations are not required if the building is fully sprinklered. Why does it seem like every office building in the DC/MD/VA area has pull stations if they're not required?
     
  2. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,722
    Likes Received:
    544
    Look at when they were built. If they were built before the IBC was first adopted, then maybe the BOCA code required them.

    Next, if they were built after the time the IBC was first adopted, look at the local amendments--they may require them regardless of sprinklered condition.

    Finally, if the other two aren't applicable, are you sure the buildings you were looking at were sprinklered?
     
  3. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    7,385
    Likes Received:
    855
    Exception: Manual fire alarm boxes are not required where the building is equipped throughout with an automatic sprinkler system and the alarm notification appliances will activate upon sprinkler water flow.

    Been in the IBC since 2003. Maybe a local amendment?
     
  4. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,453
    Likes Received:
    1,050
    As stated year built

    Or

    Fire alarm companies make money for each device sold

    Or

    Ahj talked them into installing them
     
  5. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,181
    Likes Received:
    316
    Minor correction, I seem to recall that either 13 or 72 requires a minimum of one pull station to be installed for use in the event the fire sprinkler system is out of service. I believe it has to be installed by the fire riser.

    CDA.... am I recalling this correctly?
     
  6. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,453
    Likes Received:
    1,050

    I am thinking you are right
     
  7. S.Johnson326

    S.Johnson326 Registered User

    Joined:
    Sep 5, 2019
    Messages:
    2
    Likes Received:
    0
    Thank you for the responses ! I will see what I can find In the local codes.
     
  8. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,453
    Likes Received:
    1,050

    There can be a number of reasons why pull stations are installed.
     
  9. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,126
    Likes Received:
    170
    Maryland enforces NFPA 101 as well as IBC. DC might also. I expect that most engineers in the DC metropolitan area design everything to the most stringent code of the 3, so they don't get caught leaving something out.
     
  10. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,453
    Likes Received:
    1,050

    Made me look, only because I required one pull in a non sprinkled building recently, and got my hand slapped.

    NFPA 72 2013 23.8.5.1.2
     
    Builder Bob likes this.
  11. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,181
    Likes Received:
    316
    Thanks CDA...... just ran out of memory cells and did not have time to look.

    BB
     