• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Non-structural frost wall

Ryan Schultz

Registered User
Joined
Apr 2, 2012
Messages
269
Location
Madison, WI
I know per section 1809.5 that the supporting structure needs to be below the frost line, but are there requirements, or minimum requirements for an insulated frost wall that would protect the building's slab from heaving?

Although it might hard to construct this in the field, as illustrated below, could you theoretically just put rigid insulation between the posts to protect the slab?




20180824_120817.jpg


20180824_120836.jpg
 
If the IECC is adopted, then the perimeter of the slab must be insulated to the depth indicated if in Climate Zones 4 through 8 for unheated slabs, and for all Climate Zones if the slab is heated (2015 IECC Table C402.1.3).
 
sounds good. So that "insulated wall" could be merely rigid insulation, if you could make it work in the field. Correct?

Or in other words, there's no structural requirement for that "insulated wall" if indeed, it's not structural.
 
sounds good. So that "insulated wall" could be merely rigid insulation, if you could make it work in the field. Correct?

Or in other words, there's no structural requirement for that "insulated wall" if indeed, it's not structural.
If the posts are the only load-bearing elements, then the below-grade wall is there just to support the required insulation.
 
Am confused and concerned. Am I reading this right. The treated post below the concrete will ultimately rot.
 
So it's a pole barn? Can you call it a farm building? Gets you out of the code requirements (in IL, anyway).
 
sounds good. So that "insulated wall" could be merely rigid insulation, if you could make it work in the field. Correct?

Or in other words, there's no structural requirement for that "insulated wall" if indeed, it's not structural.


If it's an IECC project, insulate to the bottom of the slab and horizontal under the first 18" (6" slab + 18" under = 2', per Table 402.1.2) of the slab edge and be done . Any interpretation of the code that would ask you to dig a trench just to put insulation in for that type of structure is way wrong.

upload_2018-8-24_14-41-22.png
 
If it's an IECC project, insulate to the bottom of the slab and horizontal under the first 18" (6" slab + 18" under = 2', per Table 402.1.2) of the slab edge and be done . Any interpretation of the code that would ask you to dig a trench just to put insulation in for that type of structure is way wrong.

View attachment 2999
The image is in reference to the residential requirements of the IBC, but the same conditions also apply to the commercial requirements in IECC Section C402.2.5.
 
Irrespective of what the code may allow, treated wood just delays the rotting of the wood. While there are some examples of old wood poles that have not rotted you will find many others that have problems.

In the proposed design it would be easy to pour a perimeter concrete wall.
 
Sure it'd be easy - but it'd be much easier to punch some holes and stick a post in them. Not to mention how much cheaper it'll be.
 
Logically, it seems like the soil below the slab in the following section could still heave and thus creak the slab.

Am I missing something? Not sure why this is an acceptable approach code-wise.


2018-12-10_14-50-13_chromeNon-structural_frost_wall__The_Building_Code_Foruchrome.png
 
Logically, it seems like the soil below the slab in the following section could still heave and thus creak the slab.

Am I missing something? Not sure why this is an acceptable approach code-wise.


2018-12-10_14-50-13_chromeNon-structural_frost_wall__The_Building_Code_Foruchrome.png
The soil under the slab is not exposed to freezing temperatures. The insulation at the perimeter is to prevent thermal bridging to the exterior.
 