• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Occupancy Classification for Townhouse: R-2 or R-3?

T-Bird

REGISTERED
Joined
May 7, 2013
Messages
95
Location
Seattle
R-2: "Residential occupancies containing more than two dwelling units"

If each townhouse is a seperate structure, than it only contains one dwelling unit. That makes it R-3, yes?
 
It is a townhouse, under the IRC, period. There is no classification.

If one were to build it under the the IBC, then yes, I would call it an R-3.

Exception: Detached one- and two-family dwellings and
townhouses not more than three stories above grade plane
in height with a separate means of egress, and their accessory
structures not more than three stories above grade
plane in height, shall comply with this code or the International
Residential Code.
 
[A] TOWNHOUSE. A single-family dwelling unit constructed
in a group of three or more attached units in which
each unit extends from the foundation to roof and with open
space on at least two sides.
 
It is a townhouse, under the IRC, period. There is no classification.

If one were to build it under the the IBC, then yes, I would call it an R-3.

Exception: Detached one- and two-family dwellings and
townhouses not more than three stories above grade plane
in height with a separate means of egress, and their accessory
structures not more than three stories above grade
plane in height, shall comply with this code or the International
Residential Code.
For fire flow modification I would need to submit the building under the IBC instead of the IRC.
 
IRC, you can install a P2904 combination system, off the domestic supply, fraction of the cost of a NFPA 13R.
 
2018 IBC 903.3.1.3 NFPA 13D Sprinkler Systems:
"Automatic sprinkler systems installed in one- and two-family dwellings; Group R-3; Group R-4, Condition 1; and townhouses shall be permitted to be installed throughout in accordance with NFPA 13D."
 
Back
Top