1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Open Web Wood Trusses in Commercial Construction

Discussion in 'Welcome Forum' started by architect629, Mar 7, 2017.

  1. architect629

    architect629 Member

    Joined:
    Dec 30, 2015
    Messages:
    1
    Likes Received:
    0
    My firm does interior fit out projects in the North East. We typically work with buildings of non-combustible construction, but we've run across a project recently that is constructed with open web wood roof trusses. I haven't had the pleasure of working with this type of construction (aside from residential) in my 15+ year career. I'm being told things by contractors bidding the projects that are "typical of this type of construction", that I'm not seeing in the code.

    Here's some info about the project.
    Type 5B construction, roughly 10,000 s.f.
    Fully sprinklered, in both the attic and occupied space.
    B occupancy with a large (>10% of floor area) storage function (S-2) which requires separation by a one hour fire barrier
    Under 2012 IBC

    I've been told by contractors that we need to install a layer of drywall on the underside of the existing wood roof trusses. I believe there's a requirement in the IRC to cover floor & roof framing, but I don't see anything in the IBC. The only thing I potentially see in the IBC is the fire blocking section. Would we need to create a fire block across the underside of the entire attic?

    The contractors are also asking if they can stop the rated partitions at the underside of the roof trusses (which would have a layer of drywall on them). This is apparently "typical". Per the IBC a fire barrier is to be continuous from the slab to the underside of the sheathing. Even if you added drywall to the underside of the truss and created a one hour rated roof assembly, the fire barrier would need to extend to the sheathing. Am I missing anything?
     
  2. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    417
    Seems to me you could use Section 503 for nonseparated occupancies
     
  3. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,871
    Likes Received:
    992
    Why are the partitions rated? In a sprinklered 1 story VB building, nothing is likely to be required to be rated....

    Don't ask me why as it makes no sense to me, but IBC allows "exits" to stop at a lid, but not other FB....

    4. Interior exit stairway and ramp enclosures required
    by Section 1022.2 and exit access stairway and ramp
    enclosures required by Section 1009.3 shall be permitted
    to terminate at a top enclosure complying
    with Section 713.12.
     
  4. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,741
    Likes Received:
    474
    Not that it helps, but in Canada, all fire rated walls can terminate at a rated ceiling provided it has the same or greater rating.
     
  5. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,871
    Likes Received:
    992
    With a sprinklered attic this does not scare me. What I am seeing now is we can build a 3 story VB apartment building with one exit stair with an unsprinklered attic over it. If the fire ends up in the attic (grill vs. siding and roof vents), it all falls in and no one gets out
     
  6. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,741
    Likes Received:
    474
    If you have proper fire dampers and fire stopping, the only way you can have a fire would be electrical in nature. Our code also requires concealed spaces to be fire blocked into certain size areas that will prevent fire spread throughout the concealed space simultaneously. If the designer chooses not to sprinkler the concealed space per NFPA 13R, the concealed space limits get smaller to account for the increase in hazard.
     
  7. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,084
    Likes Received:
    1,131
    NFPA 13
     
  8. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,871
    Likes Received:
    992
    TM...I've seen it on houses where the unattended grill lights the vinyl siding on fire, up into the soffit vent, and then the attic is on fire before anyone even knows there is a problem...HOPEFULLY management can control this in apartments, but I am skeptical....
     
  9. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,741
    Likes Received:
    474
    I think your skepticism is well placed. Our code recently started permitting mid rise combustible construction for residential and business and personal services occupancies. One of the requirements is for all balconies to be protected by sprinklers.
     
  10. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,188
    Likes Received:
    184
    This has also happened at several apartments in the Richmond area.
     
  11. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,084
    Likes Received:
    1,131


    """"""The contractors are also asking if they can stop the rated partitions at the underside of the roof trusses (which would have a layer of drywall on them). This is apparently "typical". Per the IBC a fire barrier is to be continuous from the slab to the underside of the sheathing. Even if you added drywall to the underside of the truss and created a one hour rated roof assembly, the fire barrier would need to extend to the sheathing. Am I missing anything? """"""


    Not an IBC person

    But I normally see four feet out from the rated wall, sheetrock attached to the roof deck
     