error404
Bronze Member




Project is a single family home remodeling. Under the Florida Building Code (I believe 2012 IRC would be identical for this portion of the code).
I'm most particularly interested in knowing if we comply with:
R311.7.8.2 Continuity:
Handrails for stairways shall be continuous for the full length of the flight, from a point directly above the top riser of the flight to a point directly above the lowest riser of the flight.
R202 Definitions:
FLIGHT. A continuous run of rectangular treads or winders or combination thereof from one landing to
another.
R311.7.8.1 Height.
Handrail height, measured vertically from the sloped plane adjoining the tread nosing, or finish surface of ramp
slope, shall be not less than 34 inches (864 mm) and not more than 38 inches (965 mm).
(In order to clear the design at the corner, I need place the Handrail 2" higher at each turn... so one flight is at 34", the next is at 36", and the last one at 38". Not ideal, I wish I had more space, but it's an existing stair.)
R311.7.8.3 Grip-size:
(We are going for Type I)
1. Type I. Handrails with a circular cross section shall have an outside diameter of at least 11/4 inches (32 mm)
and not greater than 2 inches (51 mm). If the handrail is not circular, it shall have a perimeter dimension of at
least 4 inches (102 mm) and not greater than 61/4 inches (160 mm) with a maximum cross section of
dimension of 2 1/4 inches (57 mm). Edges shall have a minimum radius of 0.01 inch (0.25 mm).
Anything else that I could be missing?
Thanks