• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Pool occupant load and means of egress size

Sifu

SAWHORSE
Joined
Sep 3, 2011
Messages
2,801
In a large fully sprinkled building I have a pool area on the second floor. The area has 3 exit access doors. The DP has calculated the means of egress sizing with a .3 factor. The exception to 1005.3.1 allows .2 as the factor if the building is equipped with sprinklers AND an emergency/voice alarm system. IF the building has this alarm system, and the entire building is fully sprinklered to the extent physically possible (the open air pool and deck has no ceiling on which to place sprinklers), could not the .2 factor be used?
 
If the install meets NFPA 13, you get that gimme everywhere.....In CT we think wet people are the same as dry people and do not have that gimme...
 