If a building with a protection system (alarm, sprinkler etc) is having work done, and components of a system(s) are offline due to construction, what is the usual strategy to protect the occupants while work is being done?
There is no guidance in the code I use (BCBC) but I have recently picked up NFPA 101 which has good information for this type of scenario. Just seeing what other people are doing.
Thanks
The only issue with trying to use NFPA 101 is that its only reference (in NBC 2015) is for optional use for calculating width in assembly occupancies. (3.3.2.1). So unless BCBC has other references or Acts that empower NFPA 101, you have no legal right to refer to it, and it's thus unenforceable.
As TMurray already pointed out, your traction lies in section 5.6 of the National Fire Code, which lays out a whole host of provisions:
- fire safety plan
- 1 hr fire sep in partly occupied buildings
- keeping standpipes active during construction/demolition
- etc.
Unlike NFPA 101, Section 5.6 of NFC is empowered through code.
NBC 8.1.1.1 (3) "Fire safety at construction and demolition sites shall conform to Section 5.6. of Division B of the NFC."
and, just to be detail oriented,
1.3.3.1. Application of Parts 1, 7 and 8
1) Parts 1, 7 and 8 of Division B apply to all buildings covered in this Code. (See Article 1.1.1.1.)
That gives you the legal authority to enforce construction/demolition site safety according to NFC 5.6.
NFC is free for digital download, like NBC.