• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

protective guard rail for boiler pit

michael2020

Registered User
Joined
May 29, 2020
Messages
19
Location
new york
Hi Code Masters,

I have a boiler is in a pit. Around the pit, the current protective guard is about 36" high. Shall I replace it with 42" high? Which code regulate it?

Thanks in advance.
 
1015.2 Where Required
Guards shall be located along open-sided walking surfaces, including mezzanines, equipment platforms, aisles, stairs, ramps and landings that are located more than 30 inches (762 mm) measured vertically to the floor or grade below at any point within 36 inches (914 mm) horizontally to the edge of the open side. Guards shall be adequate in strength and attachment in accordance with Section 1607.8.

Exception:
Guards are not required for the following locations:

  1. On the loading side of loading docks or piers.
  2. On the audience side of stages and raised platforms, including stairs leading up to the stage and raised platforms.
  3. On raised stage and platform floor areas, such as runways, ramps and side stages used for entertainment or presentations.
  4. At vertical openings in the performance area of stages and platforms.
  5. At elevated walking surfaces appurtenant to stages and platforms for access to and utilization of special lighting or equipment.
  6. Along vehicle service pits not accessible to the public.
  7. In assembly seating areas at cross aisles in accordance with Section 1029.16.2.

1015.3 Height
Required guards shall be not less than 42 inches (1067 mm) high, measured vertically as follows:
  1. From the adjacent walking surfaces.
  2. On stairways and stepped aisles, from the line connecting the leading edges of the tread nosings.
  3. On ramps and ramped aisles, from the ramp surface at the guard.
Exceptions:
  1. For occupancies in Group R-3 not more than three stories above grade in height and within individual dwelling units in occupancies in Group R-2 not more than three stories above grade in height with separate means of egress, required guards shall be not less than 36 inches (914 mm) in height measured vertically above the adjacent walking surfaces or adjacent fixed seating.
  2. For occupancies in Group R-3, and within individual dwelling units in occupancies in Group R-2, guards on the open sides of stairs shall have a height not less than 34 inches (864 mm) measured vertically from a line connecting the leading edges of the treads.
  3. For occupancies in Group R-3, and within individual dwelling units in occupancies in Group R-2, where the top of the guard also serves as a handrail on the open sides of stairs, the top of the guard shall be not less than 34 inches (864 mm) and not more than 38 inches (965 mm) measured vertically from a line connecting the leading edges of the treads.
  4. The guard height in assembly seating areas shall comply with Section 1029.16 as applicable.
  5. Along alternating tread devices and ships ladders, guards where the top rail also serves as a handrail shall have height not less than 30 inches (762 mm) and not more than 34 inches (864 mm), measured vertically from the leading edge of the device tread nosing.
 
An existing railing would be subject to the code it was built under. If it was built before codes were adopted then it would be subject to OSHA, as long as it's in a mechanical room that the public isn't allowed into.
 
2015 IMC - 303.7 Pit Locations
Appliances installed in pits or excavations shall not come in direct contact with the surrounding soil. The sides of the pit or excavation shall be held back not less than 12 inches (305 mm) from the appliance. Where the depth exceeds 12 inches (305 mm) below adjoining grade, the walls of the pit or excavation shall be lined with concrete or masonry. Such concrete or masonry shall extend not less than 4 inches (102 mm) above adjoining grade and shall have sufficient lateral load-bearing capacity to resist collapse. The appliance shall be protected from flooding in an approved manner.
 
thanks Ty J.
wondering if this case will full under Chapter 10 means of egress?


1015.2 Where Required
Guards shall be located along open-sided walking surfaces, including mezzanines, equipment platforms, aisles, stairs, ramps and landings that are located more than 30 inches (762 mm) measured vertically to the floor or grade below at any point within 36 inches (914 mm) horizontally to the edge of the open side. Guards shall be adequate in strength and attachment in accordance with Section 1607.8.

Exception: Guards are not required for the following locations:

  1. On the loading side of loading docks or piers.
  2. On the audience side of stages and raised platforms, including stairs leading up to the stage and raised platforms.
  3. On raised stage and platform floor areas, such as runways, ramps and side stages used for entertainment or presentations.
  4. At vertical openings in the performance area of stages and platforms.
  5. At elevated walking surfaces appurtenant to stages and platforms for access to and utilization of special lighting or equipment.
  6. Along vehicle service pits not accessible to the public.
  7. In assembly seating areas at cross aisles in accordance with Section 1029.16.2.

1015.3 Height
Required guards shall be not less than 42 inches (1067 mm) high, measured vertically as follows:
  1. From the adjacent walking surfaces.
  2. On stairways and stepped aisles, from the line connecting the leading edges of the tread nosings.
  3. On ramps and ramped aisles, from the ramp surface at the guard.
Exceptions:
  1. For occupancies in Group R-3 not more than three stories above grade in height and within individual dwelling units in occupancies in Group R-2 not more than three stories above grade in height with separate means of egress, required guards shall be not less than 36 inches (914 mm) in height measured vertically above the adjacent walking surfaces or adjacent fixed seating.
  2. For occupancies in Group R-3, and within individual dwelling units in occupancies in Group R-2, guards on the open sides of stairs shall have a height not less than 34 inches (864 mm) measured vertically from a line connecting the leading edges of the treads.
  3. For occupancies in Group R-3, and within individual dwelling units in occupancies in Group R-2, where the top of the guard also serves as a handrail on the open sides of stairs, the top of the guard shall be not less than 34 inches (864 mm) and not more than 38 inches (965 mm) measured vertically from a line connecting the leading edges of the treads.
  4. The guard height in assembly seating areas shall comply with Section 1029.16 as applicable.
  5. Along alternating tread devices and ships ladders, guards where the top rail also serves as a handrail shall have height not less than 30 inches (762 mm) and not more than 34 inches (864 mm), measured vertically from the leading edge of the device tread nosing.
 
Thanks. If we are altering it, I would think it shall be in compliance with the latest code. Which code regulates it? Building code or mechanical code? or other code?


An existing railing would be subject to the code it was built under. If it was built before codes were adopted then it would be subject to OSHA, as long as it's in a mechanical room that the public isn't allowed into.
 
I haven't seen boilers installed in pits since one-pipe steam heating systems were used. I don't see anything in the mechanical code which directly addresses this.

IBC 1015 requires 42" high guards when the walking surface is more than 30" above the surface below. Exceptions 3 & 4 to 1015.4 would allow the intermediate rail or balusters to be spaced to prevent passage of a 21" diameter sphere in this space. OSHA requirements are similar, except for requiring a toeboard so somebody walking by can't accidentally kick a tool or something lying around down onto the head of the person working in the pit..
 