1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

R507 Deck Attachment too CMU

Discussion in 'Residential Structural Codes' started by jar546, Sep 7, 2019.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    When I lived up north, I had a raised ranch and built a deck 9' off the ground but still against my CMU foundation. Back then I used staggered lag bolts into lead anchors to attach my ledger board. Behind the ledger board I used large galvanized fender washers to create a 3/8" gap for water to drain. This was in 1997 or so.

    With that being said, how would I legally attach a deck to CMU today under the IRC, specifically both R507.9 for ledger attachment and lateral connection?
     
  2. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    Would R606.11 Anchorage come into play?
    Notice the Note at the bottom of the figure.

    Screen Shot 2019-09-07 at 13.53.28.png
     
  3. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,652
    Likes Received:
    336
    self explanatory, no?
     
  4. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    No, not necessarily. Is this detail for interior only? Does it apply to exterior applications?
     
  5. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    2,095
    Likes Received:
    244
    R507.1 Decks. Wood-framed decks shall be in accordance
    with this section or Section R301 for materials and conditions
    not prescribed herein. Where supported by attachment to an
    exterior wall, decks shall be positively anchored to the primary
    structure and designed for both vertical and lateral
    loads.
    Such attachment shall not be accomplished by the use of
    toenails or nails subject to withdrawal. Where positive connection
    to the primary building structure cannot be verified during
    inspection, decks shall be self-supporting.
    For decks with cantilevered
    framing members connections to exterior walls or
    other framing members shall be designed and constructed to
    resist uplift resulting from the full live load specified in Table
    R301.5 acting on the cantilevered portion of the deck.

    Since the code does not specify how to attach a ledger to a block wall the answer is in bold above or engineered.
     
    jar546 likes this.
  6. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,046
    Likes Received:
    518
    Agree, since nothing in the deck portion of the IRC points you to R606, how can you use it?
     