I have a IIIB, mixed use R2 and S2 (parking garage) building with a 9' FSD. I want to make sure my thinking is correct:
A IIIB building requires a 2-hr exterior wall (bearing) per IBC t601. It also requires a 1-hr rated wall if the FSD is 5' to 10' per t602. So the assembly would be for a 2-hr rated interior exposure and a 1-hr rated exterior exposure. Have I missed anything?
A IIIB building requires a 2-hr exterior wall (bearing) per IBC t601. It also requires a 1-hr rated wall if the FSD is 5' to 10' per t602. So the assembly would be for a 2-hr rated interior exposure and a 1-hr rated exterior exposure. Have I missed anything?