I am reviewing plans for an existing facility that will
be replacing approx. 20 Rooftop HVAC units........The
existing HVAC curbs will remain "as is", and altered \
adjusted \ re-configured to accept the new units.
At one of the locations on the roof, the existing HVAC
unit & curbing is within 10 ft. of the edge........There
are no guards or railing installed [ RE: Section 304.11,
`15 IMC ].
QUESTION # 1: Because the HVAC equipment ONLY will
be replaced with a new unit, is the guard \ railing now
"required" ?
QUESTION # 2: There is no information on the
submitted plans regarding the installation of an electrical
receptacle "at or near the equipment location" [ RE: Section
306.5.2, `15 IMC ]......Can I "require" new electrical
receptacles "at or near the equipment locations" with the
replacement of the HVAC units ?
Please cite the applicable Code sections if your answer is
"No" to both questions.
Thanks for your input !
@ + @ + @
I am reviewing plans for an existing facility that will
be replacing approx. 20 Rooftop HVAC units........The
existing HVAC curbs will remain "as is", and altered \
adjusted \ re-configured to accept the new units.
At one of the locations on the roof, the existing HVAC
unit & curbing is within 10 ft. of the edge........There
are no guards or railing installed [ RE: Section 304.11,
`15 IMC ].
QUESTION # 1: Because the HVAC equipment ONLY will
be replaced with a new unit, is the guard \ railing now
"required" ?
QUESTION # 2: There is no information on the
submitted plans regarding the installation of an electrical
receptacle "at or near the equipment location" [ RE: Section
306.5.2, `15 IMC ]......Can I "require" new electrical
receptacles "at or near the equipment locations" with the
replacement of the HVAC units ?
Please cite the applicable Code sections if your answer is
"No" to both questions.
Thanks for your input !
@ + @ + @