• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Required Partition Rating for Gas Water Heater & Air Handler?

jms54

Registered User
Joined
May 23, 2022
Messages
3
Location
Nashville
I have a multi-family apartment project where inside each unit will be a mechanical closet to house a gas water heater and gas air handler. Where in the code do I need to look to determine the required fire rating of the walls, floor, and ceiling of the mechanical closet?
 
There is no requirement for fire ratings. However, there are requirements for clearances when adjacent to combustible construction, that typically require compliance with the manufacturer's instructions.
 
There is no requirement for fire ratings. However, there are requirements for clearances when adjacent to combustible construction, that typically require compliance with the manufacturer's instructions.
I don't think the mechanical closet would fall under incidental uses, but if it did, then that is where the required wall rating would be found, correct?
 
I don't think the mechanical closet would fall under incidental uses, but if it did, then that is where the required wall rating would be found, correct?
You would need about a 10,000 sq. ft. apartment to require a furnace that would need protection per the incidental use requirements. But even then, since a Group R requires sprinkler protection, the sprinkler system would negate the need for fire-resistive construction.
 
You would need about a 10,000 sq. ft. apartment to require a furnace that would need protection per the incidental use requirements. But even then, since a Group R requires sprinkler protection, the sprinkler system would negate the need for fire-resistive construction.