• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

roof insulation required on tenant upfit R-38?

syarn

Silver Member
Joined
Jan 20, 2010
Messages
251
Location
Philadelphia, Pennsylvania, United States
2009 IECC

2200sf type IIB assembly A-2

alteration of existing tenant space at covered mall building in austin texas to salad restaurant;

does R-38 batt have to be installed below the deck minimum if insulation is added per table 502.2 (1)?

the existing roof deck is R-6.24 and the engineer & architect directed to provide R-13 batt below deck to meet the design basis of the HVAC.

is there an exemption for alterations?
 
Insulation entirely above deck = R20ci

Metal bldgs (with R-5 thermal blocks) = R13 + R13

Attic and other = R38

If an engineer and architect are involved why would they not take the time to perform a ComCheck?
 
Yes you can convert over to U Factor

502.1.2 U-factor alternative. An assembly with a U-factor, C-factor, or F-factor equal or less than that specified in Table 502.1.2 shall be permitted as an alternative to the R-value in Table 502.2(1). Commercial buildings or portions of commercial buildings enclosing Group R occupancies shall use the U-factor, C-factor, or F-factor from the "Group R" column of Table 502.1.2. Commercial buildings or portions of commercial buildings enclosing occupancies other than Group R shall use the U-factor, C-factor or F-factor from the "All other" column of Table 502.1.2.
 
I don't think we require it if the envelope is already in place and there is not a great deal of work going on.....on second reading, I guess if you are adding anything (R13), it should comply...
 
You need to look at the locally adopted Chapter 1 scoping provisions.

See 101.4.3 of the 2009 IECC for unmodified scoping--highly unlikely to have been kept intact in adotion process.
 