AccessoryUser
REGISTERED
Dear All. We manage a building which is primarily office use. The ground floor is 9,000 SF. There is a retail unit at the entrance of the building. That retail unit has the use classification of M (Mercantile). The retail unit is c. 1,600 SF. There are four retailers in this mercantile space: a book seller, a flower vendor, a person selling cupcakes and a person selling wine by the glass (with the relevant liquor license). We placed a few tables at the centre of the retail store for customers to sit while reading a book, nibbling on a cupcake and sipping wine. The Building Code Inspector came along and ordered the removal of all seating. "Seating is occupancy Class B. This retail space is use classification M. So, remove all seating, and apply for the appropriate permit".
I am reading the Building Code and it seems that the use for a "Small assembly spaces ... shall be classified as a Group B occupancy or as part of that occupancy" (303.1.2).
So there is a choice. The use classification can be one of the following
I note that the commentary raises two further points:
I am reading the Building Code and it seems that the use for a "Small assembly spaces ... shall be classified as a Group B occupancy or as part of that occupancy" (303.1.2).
So there is a choice. The use classification can be one of the following
- Group B, or
- Part of that occupancy (i.e., Group M, in our case).
I note that the commentary raises two further points:
- The first is that Section 508.2 does not apply. "The allowances given to assembly spaces in buildings containing multiple uses reflect a practical code consideration that permits a mixed-use condition to exist without requiring compliance with the provisions for mixed occupancies (see Section 508)." That is very useful as it means that we do not have to deal with two occupancy classes. This suggests that the assembly area should always be "part of the occupancy class". If it isn't then by definition, we will have two occupancy classes: Group B, and the "main occupancy" class.
- The commentary also refers to 10% and makes it clear that the 10% does not apply "these assembly spaces are not required to be less than 10 percent of the story on which they are located (IBC Interpretation No 20-04)." I don't understand how the 10% comes in to this. There is no reference to 10% in 303.