I have an existing 2 story building that was a restaraunt ( an A-2 ) in the past,
...upstairs & downstairs dining areas.
A new owner wants to convert this building in to a Type "B" - ( Offices only )
upstairs, ...a Type "M" for part of the downstairs ( selling tennis related gear ),
and a Type "A-3" for the rest of the area downstairs.
The OL for the Type "B" area is 13 occupants.
From the most remote point in the upstairs area, the travel distance down a
set of enclosed stairs ( no elevator ), to the actual exit ( door ) is approx. 85 ft.
The entire building wil be fully sprinkled.
Table 1016.1 allows up to 300 ft. travel distance when sprinkled, for the
Type "B" upstairs.
Table 1019.1 requires 2 exits per story.
QUESTION # 1: Would the existing stairs AND a compliant EERO window meet
the requirements of the 2 exits per story, or does it have to be 2 separate doors?
QUESTION # 2: Would the travel distance in Table 1019.2, for a 2 story, Type
"B" apply ( travel distance = 75 ft. )?
Thanks for your input!
As always, please cite the various code sections. We are on the 2006 I-codes.
.
I have an existing 2 story building that was a restaraunt ( an A-2 ) in the past,
...upstairs & downstairs dining areas.
A new owner wants to convert this building in to a Type "B" - ( Offices only )
upstairs, ...a Type "M" for part of the downstairs ( selling tennis related gear ),
and a Type "A-3" for the rest of the area downstairs.
The OL for the Type "B" area is 13 occupants.
From the most remote point in the upstairs area, the travel distance down a
set of enclosed stairs ( no elevator ), to the actual exit ( door ) is approx. 85 ft.
The entire building wil be fully sprinkled.
Table 1016.1 allows up to 300 ft. travel distance when sprinkled, for the
Type "B" upstairs.
Table 1019.1 requires 2 exits per story.
QUESTION # 1: Would the existing stairs AND a compliant EERO window meet
the requirements of the 2 exits per story, or does it have to be 2 separate doors?
QUESTION # 2: Would the travel distance in Table 1019.2, for a 2 story, Type
"B" apply ( travel distance = 75 ft. )?
Thanks for your input!

As always, please cite the various code sections. We are on the 2006 I-codes.
.