1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Self-Storage Units

Discussion in 'Commercial Electrical Codes' started by Poc Building Dept, Nov 2, 2017.

  1. Poc Building Dept

    Poc Building Dept Registered User

    Joined:
    Sep 29, 2017
    Messages:
    16
    Likes Received:
    3
    Is there a requirement for exterior lighting? I have not found anything specifically outlining storage units. I see it as being an egress type of situation, although there is not a real occupant load here. I am approaching the owner with the concept for security. Any advice is greatly appreciated.
     
  2. VillageInspector

    VillageInspector Sawhorse

    Joined:
    Feb 9, 2010
    Messages:
    58
    Likes Received:
    9
    Do you have anything in your local zoning code regarding parking lot lighting? that might help you get to where you want to be.
     
    my250r11 likes this.
  3. Poc Building Dept

    Poc Building Dept Registered User

    Joined:
    Sep 29, 2017
    Messages:
    16
    Likes Received:
    3
    No, the local code has no reference to parking lot lighting.
     
  4. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,654
    Likes Received:
    836
    Poc


    Welcome again
     
  5. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,654
    Likes Received:
    836
    Might be in other city ordinances

    Check or ask
     
  6. Poc Building Dept

    Poc Building Dept Registered User

    Joined:
    Sep 29, 2017
    Messages:
    16
    Likes Received:
    3
    Seems to be no requirement. Thanks for the help!
     
  7. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,739
    Likes Received:
    653
    There is a requirement for lighting through the exit discharge, and there is always an occupant load...

    EXIT DISCHARGE. That portion of a means of egress system
    between the termination of an exit and a public way.

    [
    A] PUBLIC WAY. A street, alley or other parcel of land
    open to the outside air leading to a street, that has been
    deeded, dedicated or otherwise permanently appropriated to
    the public for public use and which has a clear width and
    height of not less than 10 feet (3048 mm).

    1006.1 Illumination required. The means of egress,
    including
    the exit discharge
    , shall be illuminated at all times the
    building space served by the means of egress is occupied.
     
  8. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,387
    Likes Received:
    223
    Self storage units? This could mean one story metal building or two story like the climate control type with stairs and egress requirements requiring lighting? I'm guessing a row of single story type buildings. For security I would request lighting, the local police may thank you.
     
  9. Poc Building Dept

    Poc Building Dept Registered User

    Joined:
    Sep 29, 2017
    Messages:
    16
    Likes Received:
    3
    Yes, single story metal building. I made the suggestion. We shall see how far it goes. Thanks for all the input everyone
     