globe trekker
- Joined
- Oct 19, 2009
- Messages
- 1,739
I have a "new" Type "M" retail store, approx. 9,200 sq. ft. ( gross ), with two
glass, sliding doors at the front entrance. The RDP has designated these
sliding doors as the 2 required MOE. Both of the doors widths are compliant
for the MOE requirements.
From the 2006 IBC: 1008.1.3.3 Horizontal sliding doors.
In other than Group H occupancies, horizontal sliding doors permitted to be
a component of a means of egress in accordance with Exception 6 to Section
1008.1.2 shall comply with all of the following criteria:
1. The doors shall be power operated and shall be capable of being
operated manually in the event of power failure.
2. The doors shall be openable by a simple method from both sides without
special knowledge or effort.
3. The force required to operate the door shall not exceed 30 pounds
(133 N) to set the door in motion and 15 pounds (67 N) to close the door
or open it to the minimum required width.
4. The door shall be openable with a force not to exceed 15 pounds (67 N)
when a force of 250 pounds (1100 N) is applied perpendicular to the door
adjacent to the operating device.
5. The door assembly shall comply with the applicable fire protection rating
and, where rated, shall be self-closing or automatic closing by smoke
detection in accordance with :Next('./icod_ibc_2006f2_7_sec015_par026.htm')'>Section 715.4.7.3, shall be installed in
accordance with NFPA 80 and shall comply with :Next('./icod_ibc_2006f2_7_sec015.htm')'>Section 715.
6. The door assembly shall have an integrated standby power supply.
7. The door assembly power supply shall be electrically supervised.
8. The door shall open to the minimum required width within 10 seconds
after activation of the operating device.
My questions are regarding requirements #2, #6 & #7.
On requirement #2: What is meant by "openable by a simple method"? If
the doors are 2 simple glass doors without any kind of hardware, or
"designed in" indentations or instructions, how can the doors be effectively
used as the MOE in a power loss, ( i.e. - they slide, not open outward ).
On requirement #6: What is meant by integrated standby power supply?
The door assembly has its own batteries? If so, who actually monitors /
checks the batteries to ensure they are not dead when needed?
On requirement #7: What is meant by "electrically supervised"?
Ya'lls input is requested! Thanks!