Rick,
I will revise my previous post a little, due to Friday headaches,
The 31-1/5" width requires a handrail to be installed, and 27" width requires two handrails to be installed, what I meant to say before was if no handrail is installed the exception is not an option, IMO.
As for the 36" travel on the required landing, the code says
R311.3 Floors and landings at exterior doors. There shall be a landing or floor on each side of each exterior door. The width of each landing shall not be less than the door served. Every landing shall have a minimum dimension of 36 inches (914 mm) measured in the direction of travel. Exterior landings shall be permitted to have a slope not to exceed 1/4 unit vertical in 12 units horizontal (2-percent).
So the way I read it, and some may disagree, if you have a landing that travels the 36" and before you get to the end of it the guard stops you, it complies, per R311.3, simply because the landing is there for the 36".
Now I know I am splitting hairs, but the codes does not say you are required to have a landing with a 36" minimum clear path in the direction of travel. Just that the landing be there.
I am guessing it looks like this but larger width
So I ask yes/no