• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Storage Rooms

kiwijbob

Registered User
Joined
Aug 26, 2021
Messages
20
Location
Canada
So as far as I can ascertain '3.3.4.3. storage rooms' refers only to storage rooms in a residential occupancy, 3.3.2.16. covers storage rooms in an assembly occupancy so if the storage room does not contain flammable liquids and/or combustible liquids no rating is required in an assembly occupancy that is sprinklered throughout.

Any thoughts?
 
You are correct. In general, storage rooms do not need a fire resistance rating. There is one fly in the ointment: the Fire Code. Depending on what is stored and if the building is sprinklered, it can drive a fire rating as well. Normally, we don't have to worry about it because it deals with large quantities of hazardous goods, but it could become an issue in larger industrial occupancies.
 