• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

T-Bar

ICE

MODERATOR
Joined
Jun 23, 2011
Messages
13,281
Location
California
23619657205_c7e5307112_b.jpg
 
Look at how that flex duct pinches down on the far left. In theory, an oblong/oval duct will have roughly the same cross section as the round duct.

In practice, this happened on one of my projects, and it restricted the airflow. I did not initially see the pinched duct installation; it had already been covered with a drywall ceiling. But shortly after occupancy, the fan coil unit was icing up, and we figured something must be blocking airflow, so they had to tear out the ceilings until they found the pinch point.
 