• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Townhome Parapet requirement?

chrisrog

Registered User
Joined
Jul 22, 2021
Messages
29
Location
Alabama
Project is a row of 6 townhomes - 2015 IRC applies.

I'm using Common walls between units with a 2 hour rating. Per R302.2.2 and R302.2.3, the rating is continued tight to the underside of the roof sheathing.
As I read the code, there is therefore no requirement for a parapet extending through the deck.

I see in R302.2.4 where you can eliminate a required parapet by sheathing the underside of the deck in Type X for 4' on either side of the common wall.

What I don't see in the code is language that defines when a parapet is required. R302.2.4 is full of language that defines the rules for parapets when they are required, but what triggers them to be required in the first place.
 
2015 IRC 302.2.2 requires parapets, then there is an exception for fire-retardant sheathing 4 feet each side or 5/8 type X. The word "shall" be constructed tells you that they are required unless you can apply the exception.
 