1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

U-factor for post frame building wall?

Discussion in 'Commercial Energy Codes' started by NerdelbaumFrinkJr, Jun 7, 2019.

  1. NerdelbaumFrinkJr

    NerdelbaumFrinkJr Registered User

    Joined:
    Jun 7, 2019
    Messages:
    3
    Likes Received:
    0
    I am designing a commercial post frame (pole barn) building in Wisconsin, climate Zone 6a. Wall construction is as follows:
    3-ply 2x8 embedded columns at 8 ft o.c., R19 batt insulation, 2x6 wall girts on exterior face, 26 gauge exterior ribbed steel, 4-mil poly vapor barrier, 2x4 girts on inside face, 29 gauge interior liner panels.

    I am familiarizing myself with the energy code requirements of these buildings, and working on envelope calculations using COMcheck. I am summing up the R-values of the wall components and determining the U-factor. I understand the ribbed steel and liner panels do not provide any insulation value.

    Is it reasonable to consider: 19 (batt insulation) + 0.83 (4-mil poly) + 1.0 (1.5" air space from the 2x4 wall girts on the inside face) = 20.83. Therefore, U = 1/20.83 = 0.048. Is this an acceptable calculation? By comparison, a wood frame wall with studs at 24" o.c. and R19 cavity insulation yields a U-factor of 0.065. Perhaps I should increase to R25 batt insulation, given that the wall cavity is 8".

    Any input or feedback is appreciated. Researching online, I have not found much on the topic of energy U-factors for post frame building walls.

    -Troy
     
  2. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,712
    Likes Received:
    239
    @ @ + @ @

    Welcome Troy, ...to the Building Codes Forum !
    Give it a few days for some other Forum members
    to respond.

    Initially, ...it appears that you DO indeed need to
    increase your thermal insulating.......Either with
    Batt type, or spray on, other.


    + + @ + +
     
  3. TheCommish

    TheCommish Sawhorse

    Joined:
    Sep 27, 2011
    Messages:
    788
    Likes Received:
    106
    What is the building going to be used for and how and how much heating or cooling energy is going to be used for the building?
     
  4. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,582
    Likes Received:
    412
    Your R-19, is that a blanket installation?

    If it is batt with framing, you need to perform a parallel heat flow calculation before the isothermal planes calculation.
     
  5. Bryant

    Bryant Registered User

    Joined:
    Dec 19, 2018
    Messages:
    16
    Likes Received:
    0
    Maybe approach it from the angle of a mass wall, composed of layers of materials, using a u factor conversion to derive at an r value. Simple cavity walls only deal with batts, but you could compond addtional layers. Even the liner panels provide some value provide there is no thermal bridging going on.
     
  6. NerdelbaumFrinkJr

    NerdelbaumFrinkJr Registered User

    Joined:
    Jun 7, 2019
    Messages:
    3
    Likes Received:
    0
    Thank you for the input. The building occupancy is S-1, unoccupied storage with no toilet facilities currently. There is no HVAC design currently. The client is increasing the wall insulation to R25 and the attic insulation to R50. In my COMcheck model, I am using a 'Other wood framed' wall assembly with a U-factor of 0.055, and the envelope criteria is satisfied (2% above code). I think that U-factor value is conservative, since a post frame wall is simply columns at 8 ft o.c., whereas a stud wall has a large percentage of framing, headers, plates, blocking, etc. that penalize the total R-value of the wall assembly.

    I will research the parallel heat flow vs. isothermal planes calculation methods.

    Thanks again!
     
  7. TheCommish

    TheCommish Sawhorse

    Joined:
    Sep 27, 2011
    Messages:
    788
    Likes Received:
    106
    if there is no HVAC why insulate the space? My recollection of the IEEC is low or no energy buildings do not requie insulation
     
  8. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    750
    Likes Received:
    17
    Ditto what TheCommish said. If no space heating or cooling, then why insulate? If the owner will insulate in the future, it may be wise to insulate the building now before the energy code becomes more stringent.

    Last I knew, COMCheck used the parallel flow method for U-value calculations, so that is what I use to comply with COMCheck. Parallel flow calculates a higher U-value than Isothermal. I use an average value from the parallel and isothermal methods when calculating heat loss / heat gain.
     
  9. NerdelbaumFrinkJr

    NerdelbaumFrinkJr Registered User

    Joined:
    Jun 7, 2019
    Messages:
    3
    Likes Received:
    0
    The owner will add restrooms and possibly have offices in the future, possible some light manufacturing (F-1) too. I think the equipment/materials being stored require a somewhat regulated environment, so he is insulating now.
     
  10. Bryant

    Bryant Registered User

    Joined:
    Dec 19, 2018
    Messages:
    16
    Likes Received:
    0
    Tenant shell !
     
  11. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,857
    Likes Received:
    197
    2015 IECC C503.2 Change in space conditioning. Any nonconditioned
    or low-energy space that is altered to become conditioned
    space shall be required to be brought into full compliance
    with this code.

    You can't know what insulation to use unless you are conditioning it before the next code cycle is adopted. Sometimes it changes.
     